        I want to put power flushing toilets in my building but to do that have to go from a 2″ to 3″
        water lines. I do not want to put those Sloan power tank flushers the ones that have a tank within a tank
        those are a maint. problem
        So I’m looking for some alternat piece of equipment.

      • #286736
        Avatar photoSylvanLMP
        Participant

          Sir the “normal” size supply line to the “power assisted tank” is 3/8th of an inch.( not including the severe restriction the globe valve causes with a 1/4″ opening in many cases.)

          Using a 2″ supply pipe (Riser) I could take off 28.5 3/8 pipes to get the same volume.

          With a 3″ line I could supply 62+ toilets with a 3/8 supply to get the same volume.

          Are you sure your not thinking of a flushometer, like the Sloan Royal 110 etc instead of the Sloan Flushmate (Pressure assisted tank bladder) Good Luck in your Quest