baseboard heating requirements

Home Forums Public Forums Estimating & Costing baseboard heating requirements

Viewing 1 reply thread
  • Author
    Posts
    • #279593
      Avatar photoAnonymous

        What total lenght of baseboard heating do I need for 1000 square feet of living space in a finished basement in Connecticut with 2/4 fiberglass insulated walls.

      • #301269
        Avatar photoGuest
        Participant

          THIS ONLY A RULE OF THUMB B&G HAS
          A SIMPLE HYDRONIC MANUEL
          I USE 50 BTU / SQ FT WHICH ON THE
          HIGH SIDE IE A BASEMENT 50 20
          = 50,000 BTU = DIVED THAT INTO
          BTU PER LINEL FOOT OF BASEBOARD
          AT 180 DEG 730 BTU =68 FT OF
          BASE BOARD