Minimum size of vent required

Home Forums Public Forums Drainage & Sewerage Minimum size of vent required

  • This topic has 4 replies, 4 voices, and was last updated 23 years ago by Avatar photoSylvanLMP.
Viewing 4 reply threads
  • Author
    Posts
    • #279026
      Avatar photoMasterPlumbers
      Keymaster

        I need to run a new vent for a water closet, lav and bar sink. There is an existing 2″ vent for another water closet and lav. Can I connect to this vent is my question???

      • #299822
        Avatar photoSylvanLMP
        Participant

          Ah Mike dont you just wish plumbing were that simple guy?

          Venting is not just fixture units connected BUT developed lenth of pipe and fittings.

          For example I could run 8 FU’s on an 1-1/2 line BUT only for 30 ft BUT I would need a 2″ line to go up to 170 ft.

          Did you now depending on what type of toilet you have how many fixture units it is rated at?

          For example a close couple tank and bowl would be 4 FU and a flushometer type would be 6 FU..

          Why dont you invest in a local code book rather then guessing?



          SylvanLMP

        • #299823
          Avatar photoGuest
          Participant

            Its to bad plumbers do not have a code book thats close to the same in this country. Respect comes from organisation. In CT you can vent 102 DFU (16 bathrooms) on one 1 1/2 vent pipe 30 ft.

          • #299824
            Avatar photoRobert Stephen Morton
            Participant

              Mr Unity. We lowly Plumbers in Oz work on a rating system for vents, that is :-

              Size of Fixture units Vent rating
              vent pipe discharging to
              DN drain

              40 >1 <10 .5
              50 >10 <30 1
              65 >30 <175 2
              80 >175 <400 3
              100 >400 6

              If there are other vents on the line they can be used as credits. ie 12 40mm vents off a stack could be equivelent to a 100mm vent venting more than 400fu, However we have to get the sewage to run uphill.

            • #299825
              Avatar photoSylvanLMP
              Participant


                In reply to message posted by unity:
                Its to bad plumbers do not have a code book thats close to the same in this country. Respect comes from organisation. In CT you can vent 102 DFU (16 bathrooms) on one 1 1/2 vent pipe 30 ft.


                Is this a local code like Danbury or a state code?

                102 FU’s seems like a lot on a 11/2 pipe ESPECIALLY in a movie theater where it would be quite possible all fixtures being used at once during an intermission.

                The over loading of the vent would be unbelievable with back pressures.



                SylvanLMP