Sewer gas in basement bathroom

Home Forums Public Forums Drainage & Sewerage Sewer gas in basement bathroom

Viewing 1 reply thread
  • Author
    Posts
    • #279017
      Avatar photoMasterPlumbers
      Keymaster

        I recently had a basement bath installed. Works OK except everytime the sewage ejector pump fires it syphens the traps of the shower and sink allowing sewer gas to seep up. I know there is a problem with the way it is vented, but I’m not sure exactly what needs to be done to fix it. Any suggestions???

      • #299798
        Avatar photoSylvanLMP
        Participant

          Have someone install a proper vent AT THE SEWERAGE EJECTOR. SEE Stevens or Nossiter pumps for a proper installation.

          Some sewer gases are linked some types of Cancers