toilet flange elevation

Home Forums Public Forums Drainage & Sewerage toilet flange elevation

Viewing 1 reply thread
  • Author
    Posts
    • #278868
      Avatar photoMasterPlumbers
      Keymaster

        trying to figure floor slab elevation with an existing septic tank, I know about the 1/4 per foot slope. my question is: How much room to I need between the flange and the bottom of the curve fitting into the waste stack. This measurement will determine how many course of block needed above ground grade elevation. I,m looking at the farthest distance of 47 feet from tank.

      • #299469
        Avatar photofourth year
        Participant

          i am not sure which measurement you are requesting, but the minimum distance from the floor to the bottom of the lateral pipe at a toilet is 19″.