Distance between LPG Cylinder and electric Hot Water Service

Home Forums Public Forums Gas & Gasfitting Distance between LPG Cylinder and electric Hot Water Service

Viewing 1 reply thread
  • Author
    Posts
    • #278374
      Avatar photoMasterPlumbers
      Keymaster

        Each would be enclosed in their own cabinet (timber/cement sheet) but wondering if there is a minimum distance required between the two units.

      • #298405
        Avatar photoPLUMBILL
        Participant

          If the tank is 125 gallons or less you just need 3′ spacing per ICC and 5′ of spacing for ASME requirements, your supplier should know what standard you must meet.

      Viewing 1 reply thread
      • You must be logged in to reply to this topic.

      Pin It on Pinterest

      Share This