The McDonnell & Miller Model 47 boiler feed float on my steam boiler doesn’t always stop the water input. It seems to stick but when I push on the lever mechanism it works for a while. I drain it periodically to clean out the rust & sprayed wd40 on the external pivot points.
Is there anything else I can try? Does the float go bad on these after 15-20 years? If I replace the unit, do I try & disassemble & replace the float, or just the black ball unit, or the whole assembly including the cut off & the square thing below the cut off?
Thanks in advance
Ron
-
10 Oct 2005 at 10:10 pm #296914Retired plbg1Participant
http://www.statesupply.com/displayCategory.do?Id=764
Try this ite they have your parts, maybe you just need new washer inside, let me know.
Art retired plbg -
24 Oct 2005 at 10:47 pm #296915cove3Participant
Success. I figured out why the boiler feed cut off float wouldn’t stop the flow of water to the boiler. I found that the cast iron float bowl was full of sludge/rust which was reducing boyancy and jamming the lever from closing the valve.
Unfortunately I found this out after buying a new McDonnell 47-2 unit at $470, installing it, and then taking apart the old unit.
All I had to have done with the old unit is unscrew the 4 bolts at the bottom where the weekly drain of water comes out and it would have allowed me enough of a look to have seen the sludge which I could have scraped out with a screwdriver and flushed out.
In the process, I discovered that there’s a screen that needs to be cleaned yearly, which my boiler service people never did. It was full of crud also. I also found out that the new 47-2 unit has a design change from my old one so that the screen and the shut off valve are both removable from the bottom of the unit.
I would think that since most people don’t properly flush out the float unit weekly as recommended, that this would be a common problem with steam boilers. Hope my experience saves others a service call and purchase of a new unit. Done correctly, it would be at most a 1 hour job to clean both the float chamber and the screen.
Regards, Ron
-
-