hot and cold suppys

Home Forums Public Forums General Plumbing hot and cold suppys

Viewing 3 reply threads
  • Author
    Posts
    • #277295
      Mario Blas

      when installing new hot and cold supply lines thru new tgi beams what is a good spacing distance side to side and from the bottom of the tgi up?I know from some experience that getting long lengths in is more difficult

    • #295937
      Retired plbg1
      Participant

      If you are drilling holes in them make sure you use thse inserts and I would make them 6 or 8″ apart so if you have to cut pipe you have room for cutters, dont run them less then 4″ apart.

    • #295938
      epacertified1
      Participant

      whats inserts?
      how high should holes be drilled ?(just for easy pipe installing)

    • #295939
      Retired plbg1
      Participant

      Inserts are pvc rings that fit into hole after you cutit, you put them on pipe and after pipe is in you push them into the hole, you dont have to use them but make sure you make hole big enough for pipe to expand and also hang it every 8′ at least 2-1/2″ from bottom of joist.

Viewing 3 reply threads