New water heater banging away…

Home › Forums › Public Forums › General Plumbing › New water heater banging away…

Viewing 16 reply threads
  • Author
    Posts
    • #277159
      Avatar photoGarrett Lane
      Member

      Hello everyone,

      We just had a new Hotpoint 40 gallon, gas, direct vent
      water heater installed.

      When the cold water is shut off anywhere in the
      house, by us or an appliance, a loud metallic bang can be
      heard coming from the water heater, followed
      by three or four additional knocks which get softer until they
      stop. It sounds like something is swinging inside
      the water heater and hitting something over and
      over again.

      No noise is heard when the hot water, or a mixture
      of hot and cold water is shut off. Only straight cold water.

      Could the drip tube be smashing into something, or do you have
      any other ideas?

      Thanks for the help!

      » This message has been edited by UTahJ on 28 January 2004

    • #295566
      Avatar phototurdchaser
      Participant

      Most likely one of two things,
      First and most common is a valve that is not completely closing. Turn the water off to the clotheswasher and see if it goes away, then turn the water of to the toilets and see if it changes. If this does not isolate it the next most common possibility is that you have a closed domestic water system. Being that there is either a backflow preventor or pressure regulator on the incoming line. As water heats up in the tank it expands and pressure buildsup because it can not desipate into the water supply system because it is closed. The excess pressure will make all sorts of noise when valves are operated. Most likely the first scenario will fit. Let us know!

    • #295567
      Avatar photoUTahJ
      Participant

      Thank you for the reply.

      I tried turning off the supply to the washing machine,
      and the toilet separately, and then I tried them together.
      (we don’t have anything else that would use cold water
      other than the kitchen and bathroom faucets), but the
      banging in the water heater persisted.

      It appears to be a closed loop system as you stated,
      however there isn’t a pressure regulator or backflow
      preventor visible inside the house. The line exits
      through the basement floor and runs about 20 feet
      to the city shut off valve in the front yard. And the rest
      of the system is just plain old copper pipe.

      The noise wasn’t present with the old water heater
      we had, but that thing wasn’t very efficient either, so
      maybe thermal expansion wasn’t an issue.

      Any other suggestion?

    • #295568
      Avatar photoSelgas
      Participant

      Fairly certain that your problem is related to a loose fitting pipe on your water line somewhere that is not properly clipped or strapped.
      Simply, when you close a tap under mains pressure the shock wave causes a vibration we call water hammer within pipes on ocassions. This is usually more commonplace with appliances that have fast opening or closing solenoid valve that “slam” shut causing the shock wave in the piping system. If you cannot locate the loose pipe you can fit a device into the water line called a water hammer arrestor that will do the job for you.
      You should also check and make sure that the water heater has a pressure limiting valve fitted on the inlet cold water line to it – the purpose of this device is to ensure that water pressure does not exceed that to which the water heater relief valve has been set, thereby no stressing any other valves within the system.



      Selgas Services Ltd
      Craftsman Gasfitters, Plumbers, Electrical Service Technicians

    • #295569
      Avatar photoUTahJ
      Participant

      Thanks for the reply Peter.

      The noise is definitely coming from inside the
      water heater. I don’t hear any noises from the
      rest of the piping in the system.

      I tried putting the smaller, bladder type, water
      hammer arrestors on the toilet, kitchen sink,
      and the washing machine cold water lines this evening,
      but they didn’t do a darn thing. Maybe I should
      have tried them on the hot water side, but I got
      discouraged by the inital results on the cold side.

      You’re idea about a pressure limiting valve on
      the hot water inlet might be my only choice.
      My only concern is that I played around with adjusting
      the cold water inlet valve on the water heater, to
      see if I could eliminate the bang. The only time
      it disappeared was when the cold water was almost
      all the way off, thereby reducing our hot water pressure.

      I’ll check into the value though… I’m sure what ever
      is making the noise in the water heater is bound to
      break eventually… not a good thing.

      Thanks again!

    • #295570
      Avatar photoDUNBAR
      Participant

      http://www.wattscanada.com/faq/regulators/main.html
      http://www.wattsreg.com <<<< click on products, then thermal expansion..........this is a recommended item on a closed system.
      Once you know your water pressure, then make the decision to go with the PRV………which should be on the main water line immediately following the main shut off valve to protect the entire plumbing system, hot and cold.

      » This message has been edited by DUNBAR on 29 January 2004

    • #295571
      Avatar phototurdchaser
      Participant

      The next step I would take is to turn the gas off and run water to let the tank cool down. Then see if the problem is still there, this will give us an idea if the cause is coming from outside of the water heater or is being generated from inside the tank.

    • #295572
      Avatar photoUTahJ
      Participant

      turdchaser:

      I liked your idea, so I tried it as soon as I got
      home. I shut off the water heater and ran the hot
      water until it ran cold. Guess what… same noise.
      I guess that rules out thermal expansion problems.

      So I’m assuming I have water pressure that’s high
      enough to make something in my hot water heater rattle
      around when a faucet is turned off.

      Two more questions before I call the plumber back:

      1. If I had to turn the cold water supply to the water
      heater almost all the way off before the bang stopped,
      wouldn’t I have to set the pressure reducing valve
      to such a low PSI that it would be unbearable, just
      to acheive the same effect?

      2. What are the odds that the water heater we purchased
      is just faulty, with something loose inside?

      Thanks for everyone’s help!

    • #295573
      Avatar phototurdchaser
      Participant

      Yes, exactly. We have eliminated thermal expansion as well as the noise that air escaping from the water in a gas water heater makes as it heats up. The likelyhood of the tank being faulty and causing it is low. It is possible but very unlikely. Personnally I have had guys drop tanks and there be visible damage to the outside. I have turned around and sold them at a loss and personnally backed up the warranty and have yet Had a problem with one. This is why I say it is possible but unlikely. Have the plumber inspect the water supply piping for any causes and if none are found the following product is your best bet to fixing the problem. It should be installed on the cold water supply just before the tank. http://www.amtrol.com/website/content.nsf
      click on homeowner general info., click products red button, click residential, expansion tanks then therm-X-Trol
      Do let us know how it turns out when you get it fixed.

      » This message has been edited by turdchaser on 30 January 2004

    • #295574
      Avatar photoSelgas
      Participant

      Ahhhhhh ha from your last post I would not be surprised to find the fault being a broken off or very loose hanging anode rod or dipper tube in the cylinder itself – if these were at fault then the noise would only be evident when hot water was being run or when a hot tap was turned off.
      These problems on a new cylinder would indicate to me that it had been mistreated when being transported. Both of these components can be easily changed or checked as they either screw into the cylinder or fit inside one of the water connections.
      The problem you have explained is less likely to to be pressure related but more something amiss within the tank itself.



      Selgas Services Ltd
      Craftsman Gasfitters, Plumbers, Electrical Service Technicians

    • #295575
      Avatar photoUTahJ
      Participant

      Peter,

      It sure sounds like the anode rod is hitting something,
      because it is definitely a metal on metal sound, but
      it doesn’t happen when the hot water is used, or
      when hot water is mixed with cold. It only happens
      when cold water is used.

      Most drip tubes are plastic now, aren’t they?

      Thanks again!

    • #295576
      Avatar phototurdchaser
      Participant

      All dip tubes are plastic now. The anode rod is a stiff approx 1/8th in. rod that hangs down from the nut it is secured to. The only other thing inside a gas tank is the the combination gas, thermostat valve which screws into the side of the tank. If you wish to remove the anode simply depressurize the hot water and drain a little water out of the tank and unscrew it, cut it off of the nut and screw the nut back into the hole. By removing it you will decrease the life of the tank.

      » This message has been edited by turdchaser on 31 January 2004

    • #295577
      Avatar photoUTahJ
      Participant

      turdchaser:

      Thanks for the info. I think I’ll run down to the hardware store to see if they have a “bolt” that
      will act as a temporary plug after I pull the rod out. I don’t want to destroy the rod, I just want to eliminate
      it as a possible cause of the noise.

      I suppose a replacement rod would have to be
      ordered through Hotpoint, eh?

    • #295578
      Avatar photoDUNBAR
      Participant
    • #295579
      Avatar photoRetired plbg1
      Participant

      Did you check and see if washer is loose on your CW valve going to Wh are any other valve in house including toilets.



      Art retired plbg

    • #295580
      Avatar photonicktheplumber
      Participant

      I suspect that you have excessive pressure from your house water main, and that there is probably nothing wrong with your water heater. You probably tee’d off your house cold water lines from your WH cold inlet, and when a cold fixture valve shuts you are getting water hammer transmitted back to your WH. You should ahve a pressure limiting valve at the entrance of the supply line to your house. If not, intall one. As regards water hammer, you can install water hammer arrestors at each fixture, or better yet, install a multitube arrestor on the supply line where it enters the house. And, of course, make sure that all of your pipes are securely held to the structural members of your house.

      Finally, you could install an expansion tank atop your WH, but this helps only if your noise is due to hot water expansion, which you state you have ruled out.

      NtP