      I need to know where dielectric couplings would have to be installed and their purpose and alternative methods.Have searched codes ect,help would be greatly apperciated.

    • #294530
      Avatar photonicktheplumber
      Participant

      The simple answer to your question is that dielectric couplings need to be installed at ALL connections between ferrous (iron/steel) pipe and copper pipe. These couplings place an insulator (otherwise known as a “non-conductor” or “dielectric”) between the two types of pipe. Without this insulation between the two metals, an electrochemical reaction (called “Red-Ox” or “reduction-oxidation”) will occur, leading to corrosion of the pipes and leaks. Red-Ox reactions depend on a basic physical property of the metals, called “Red-Ox Potential.” This is the kind of stuff you learn in high-school chemistry, and I’ve forgotten most of it. Iron and Copper have enough Red-Ox potential difference to cause problems in a plumbing system.

      Various commercial dielectric fittings are available, mostly unions and things like those flex fittings used to connect water heaters. A commonly accepted alternative to a true dielectric fitting is the use of a yellow brass nipple to connect the two types of metal, especially in the case where a brass valve is to be connected to galvanized iron pipe. Screwing a galvanized pipe directly into a brass valve leads to corrosion and leakage, but the use of a yellow brass nipple between the two seems to work quite well.

      NtP

    • #294531
      Avatar photobooberry
      Participant

      thank you nick! You gave me some good info and it helped alot.

Viewing 2 reply threads
  • You must be logged in to reply to this topic.