Home Forums Public Forums General Plumbing Wtare heater relief discharge

Viewing 8 reply threads
  • Author
    Posts
    • #276166
      Avatar photoMasterPlumbers
      Keymaster

        Today my water heater began discharging hot water from the relief valve. When I saw it, it had probably relieved a gallon or two of water outside. I am on a well and pressure tank, the water heater is propane fueled. I turned the temperature down on the heater as it was turned up high. For some reason I turned on the hot water in the sink too. It stopped discharging soon after.

        This is the 1st time this happened. It is fairly new. What is the most likely reason for this.

        Thanks in advance.

      • #293544
        Avatar photoRetired plbg1
        Participant

          Sometimes when water is heated fast it has to expan and builds up pressure so it goes out the valve, thats for saftey.

        • #293545
          Avatar photorobertgf
          Participant

            unless the water was heated to 210 degrees the relief valve would not go off on temp. you probably have a pressure problem due to thermal expansion that needs to be addressed turning the temp down might lessen the problem but will not eliminate

          • #293546
            Avatar photooscar
            Participant

              No wonder you are retired,Mr retired plbg.,some of your replies are just plain stupid.

            • #293547
              Avatar photoRetired plbg1
              Participant

                Oscar
                If you dont like my replies then dont read them and keep your mouth shut.

              • #293548
                Avatar photooscar
                Participant

                  I didnt say a word.I type with my fingers,not my mouth

                • #293549
                  Avatar photomikeinpa
                  Participant

                    Do you two know each other

                  • #293550
                    Avatar photoSelgas
                    Participant

                      Ok you lot it’s my turn to try and assist this fellow so here we go.
                      Firstly the valve you are referring to is called a TPR valve (temperature and pressure relief) it is designed so that is the water rose to a temperature greater than 99 degrees C, or the water pressure exceeded the valves rated specifications then it will open and discharge or release the pressure via the valve to waste.
                      However, with over 35 years experience with gas fired water heaters it is commonplace for this to happen on ocassion due to the extreemly rapid heat up capability of the gas burner used in the water heater.
                      To overcome this problem install a pressure limiting valve on the inlet to the cylinder and a cold water releif valve on the same line rated at 70% of the maximum setting of the hot water relief valve. This will allow the expansion to discharge cold water when the main burner is firing and keep your gas operating costs to a minimum.
                      Hope this helps.



                      Selgas Services Ltd
                      Craftsman Gasfitters, Plumbers, Electrical Service Technicians

                    • #293551
                      Avatar photooscar
                      Participant

                        Alright peter,see tired plbg,thats an intelligent answer.