baseboard heat pressure problem

Home Forums Public Forums General Plumbing baseboard heat pressure problem

Viewing 4 reply threads
  • Author
    Posts
    • #276070
      brijude

      Lately I have been having a problem with the pressure on my expansion tank. Usually in a heating season I will bleed my pipes and drain my expansion tank about twice. Lately the pressure has been increasing into the danger area on my gauge and I have been draining my expansion tank a least 2 times a day. This started when the main water was shut off during a plumbing problem. Is there a way I could fix this or am I in trouble?undefined

    • #293366
      Harold Kestenholz
      Participant

      You have lost the seal of your system against the loss of air. When you have the type of system with an expansion tank that must be drained, it is called an air control system. If you have automatic vents or other openings in the system, or change to a high-head pump on the return, you can start to lose the air that must return to the expansion tank. Your system was not well-controlled in the past because you had to drain the tank twice per year, now the problem has accelerated.

    • #293367
      hc117
      Participant

      Does this mean I need to replace my system or can it be fixed?

    • #293368
      Harold Kestenholz
      Participant

      You need to find the air leak and fix it and/or you need to find a way to return the air that leaves the tank.

    • #293369
      hc117
      Participant

      Thank you, have a nice holiday.