        I recently installed a pressure balance faucet assembly in my shower and now the pipes bang whenever i use any faucet in the house. I am assuming all the air is out by now .
        All the pipes are tite there are hammer tubes on the shower. HELP this is really anoying and the wife she aint happy any sugestions.



        Thanks
        Jack Of All Trades

      • #292881
        Avatar photoTheLocalPlumber
        Participant

          Dear expert of none,
          Check the water pressure, if over 70# install a pressure reducing valve.
          Replace the hot and cold washers on the faucets.
          That should take care of it.
          Bill