        have hot water no leaks at sweated and threaded connections…but water still accumulates at base of tank….any thoughts??? :

      • #292511
        Avatar photoNickHydro
        Participant

          Gravty maks the water flow downhill. Yuo might need a tank to letr water expand as it heets up.

        • #292512
          Avatar photoBruce T
          Participant

            pull the little plastic cover from around the factory installed drain and check the threads, as well as the factory installed T and P valve, anode rod and maybe where the gas valve is screwed into the tank. ..sometimes even the factory screws up!
            and check the discharge of the T&P valve because of thermal expansion…
            I think thats what NICK is saying…HAHAHA!