Dielectric Union or Not?

Home Forums Public Forums General Plumbing Dielectric Union or Not?

Viewing 5 reply threads
  • Author
    Posts
    • #275346
      Avatar photoAquarian

        I have an oil fired residential boiler. I have noticed that there are no dielectric unions installed between the 3/4″ copper pipe heating pipes and the black steel NPT threaded pipes in the boiler’s supply or return side piping. There is no dielectric union used also for the cold water supply to the boiler. Should there be dielectric unions in any of these locations?

        Joe

      • #291751
        Avatar photoTheLocalPlumber
        Participant

          Joe, Dielectric unions are a thing of the past. In fact they may cause more harm then help. The new code editions do not include dielectric unions, they recommend a seperation be used with a piece of brass piping not to be less then 6″.
          Good Luck to you,
          Bill
          The Local Plumber
          Tustin, California http://www.TheLocalPlumber.com

        • #291752
          Avatar photojoecarjoe
          Participant

            Thanks for the info Mr. Local Plumber.

          • #291753
            Avatar photoSylvanLMP
            Participant

              You do not need isolation fittings like a dielectric unions or nipples when mixing ferrous and non ferrous metals like copper to black pipe ESPECIALLY in a closed system where little or no oxygen is present.

              Think about the following

              Steam System Black steel with cast Iron radiators and BRASS valves.

              Fire suppression piping BLACK STEEL Brass OS&Y valves and BRASS sprinkler heads.

              Gas piping Black steel Brass gas valves.

              Water Mains Cast Iron class 22 with copper Type K gooseneck connections

              Fire hydrants cast Iron Brass nipples for the fire hose connection.

              Depending on the type of service and piping materials like copper/brass, etc., connected to a galvanized line here could be a major problem.

              Closed hot water or chilled water system not a problem as long as your not mixing zinc.

              This was a major problem in by gone days when folks trying to conserve copper made an alloy called yellow brass in stead of red brass.

              The red Brass 85% copper 15% Zinc gave years and years of trouble free service BUT the yellow brass 60% copper 40% Zinc had all kinds of problems like becoming brittle like due to dezinification

              Using a dielectric fitting is not a bad idea but in this case it really is not warranted UNLESS you have a major make up problem where fresh water (lots of oxygen) is in this system as Oxygen in water is what destroys ferrous metals under most conditions.

              Even the older cast Iron water mains are protected by use of hot applied Coal tar enamel.

              The better codes (not the codes where officals who are being paid off by some home builders) do want some type of protection where a conditions may exist where a premature piping failure may occur do to mixing various materials.

            • #291754
              Avatar photoSylvanLMP
              Participant

                You do not need isolation fittings like a dielectric unions or nipples when mixing ferrous and non ferrous metals like copper to black pipe ESPECIALLY in a closed system where little or no oxygen is present.

                Think about the following

                Steam System Black steel with cast Iron radiators and BRASS valves.

                Fire suppression piping BLACK STEEL Brass OS&Y valves and BRASS sprinkler heads.

                Gas piping Black steel Brass gas valves.

                Water Mains Cast Iron class 22 with copper Type K gooseneck connections

                Fire hydrants cast Iron Brass nipples for the fire hose connection.

                Depending on the type of service and piping materials like copper/brass, etc., connected to a galvanized line here could be a major problem.

                Closed hot water or chilled water system not a problem as long as your not mixing zinc.

                This was a major problem in by gone days when folks trying to conserve copper made an alloy called yellow brass in stead of red brass.

                The red Brass 85% copper 15% Zinc gave years and years of trouble free service BUT the yellow brass 60% copper 40% Zinc had all kinds of problems like becoming brittle like due to dezinification

                Using a dielectric fitting is not a bad idea but in this case it really is not warranted UNLESS you have a major make up problem where fresh water (lots of oxygen) is in this system as Oxygen in water is what destroys ferrous metals under most conditions.

                Even the older cast Iron water mains are protected by use of hot applied Coal tar enamel.

                The better codes (not the codes where officals who are being paid off by some home builders) do want some type of protection where a conditions may exist where a premature piping failure may occur do to mixing various materials.



                SylvanLMP

              • #291755
                Avatar photoGuest
                Participant

                  Dear Mr Sylvan,

                  Thank you so much for your wonderful comments. I really enjoy reading your postings and you are a very remarkably intelligent man. I enjoy both your wit and your knowledge and look forward to reading your postings in the future……
                  Thanks Again,
                  Susan
                  South Florida