        I have a shallow well,When my pump calls for water, It will run for quite a while ( 5 or so minutes then shutts off automaticly.
        I also have atrol bladder holding tank.
        My well is 150 feet or so away from my pump in the house.
        Just recently the pump runs for a lot longer than usual, but wont shut off unless I shut off switch and when I turn it right back on then it will shut off on its own.
        what do you think is wrong ,Pressure switch?
        And should my pump take that long to fill holding tank?
        Any help or suggestions would greatly be appreciated,Thank you in advance.

      • #291576
        Avatar photomarcelg
        Participant

          Sounds like a partialy blocked venturi jet.

          Marcel

        • #291577
          Avatar photodaveroconn
          Participant

            Your storage tank may have lost it’s air pre-charge. You need to check the tank and make sure that this is not the problem first before checking any other component of your water system.

            If you are getting air from your expansion tank then the bladder inside has failed DO NOT DRINK THE WATER the following is how to check the tank.

            The only way an expansion tank can drain is for air behind the bladder to push it out. If your tank does not drain completely than it does not have enough air in it to displace the water inside. You should be able to easily move the tank empty.

            To drain an expansion tank

            First you need to drain the tank as far as it can go by itself. Next using a bicycle tire pump fill up the tank only until the water begins to flow out. Do not over pump the tank or you may ruin the bladder. Keep doing this until you are sure all of the water is out of the tank. Now to obtain the proper air pressure this can only be checked with the tank empty. Fill the tank up with 2 psi below the start of your pressure switch. (Example 30 psi on means 28 psi in the tank.) If the tank will not hold this pressure then the bladder has failed.

            Now it would be a good time to disinfect the tank with some bleach. Use an empty filter sump housing to introduce about a 1/4 cup of bleach into the tank you will need some valves to do this. Now rinse the tank by filling it and draining it several times.

            Respectfully David F. Walling