jet pump/check valve installation problem

Home Forums Public Forums General Plumbing jet pump/check valve installation problem

Viewing 2 reply threads
  • Author
    Posts
    • #275025
      Avatar photoAndrew E. Uhas

        Following installation of a check valve in the line leading from a water-well jet pump, the pump turns on momentarily every time a faucet is turned on. The storage tank pressure indicates the maximum set-point. Should the set-point switches be located at the jet pump (where they are now) or after the check-valve location (on the side near the storage tank)? Also please explain the answer.

      • #290956
        Avatar photodaveroconn
        Participant

          Place the pressure switch after the check valve on the discharge side of the pump. Place it on the branch side of the tee just before the storage tank. Pump is pulling water from well, when pump is in off position check will be pulled shut by the water running backwards toward the well. Pump would then come on with the pressure drop (faucet being turned on) and then off again because the storage tank is already full of water.

          Respectfully David F. Walling

        • #290957
          Avatar photogranchio
          Participant

            quote:


            Originally posted by daveroconn:
            Place the pressure switch after the check valve on the discharge side of the pump. Place it on the branch side of the tee just before the storage tank. Pump is pulling water from well, when pump is in off position check will be pulled shut by the water running backwards toward the well. Pump would then come on with the pressure drop (faucet being turned on) and then off again because the storage tank is already full of water.

            Respectfully David F. Walling


            Many thanks for your answer and clear explanation. In the original configuration, the pressure switch is a part of the pump; looks like that will have to be disabled with a new switch added (at the tee), then rewire the pump to it. The check valve was put in right up against the inlet on the tee so guess will have to put a “T” connection on the tee since there is a pressure relief valve where the switch would normally be.