Backflow Assembly Testing

Home Forums Public Forums General Plumbing Backflow Assembly Testing

Viewing 3 reply threads
  • Author
    Posts
    • #274220
      Avatar photoAnonymous

        I have a backflow RP assembly that is installed on a well head. In order to properly test an RP assembly there must be water pressure at all time on the inlet side of the device. Since the assembly is installed on the well head the only time there is pressure is when the pump is running. It is a submerssable pump and it is not good for it to deadhead it. The testing involves closing the #2 shut off valve for some time, thereby causing the pump to “deadhead”. Does this assembly have to be relocated to a point after the pressure tanks or is there a way to test it I am not aware of?

      • #289389
        Avatar photoSylvanLMP
        Participant

          Contact the ASSE for their recommendations. give them the model and make of your device

        • #289390
          Avatar photofourth year
          Participant

            Check with your pure water control board, but I would assume they would require that it be installed after the tanks, otherwise a potential backflow situation would contaminate the tanks.

          • #289391
            Avatar photoGuest
            Participant

              The correct placement for the RPZ backflow preventer is in the water supply line which is usually immediately downstream of the main valve from the storage tank(s). The well is actually the source and shouldn’t be confused with the supply.
              Is this a farm application? For proper protection of all components of the pressure system, including the well, you may need a combination of devices and piping considerations to provide adequate protection.