baseboard hot water heat

Home Forums Public Forums General Plumbing baseboard hot water heat

Viewing 1 reply thread
  • Author
    Posts
    • #274165
      MasterPlumbers
      Keymaster

      How do I bleed the air out of a hot water baseboard unit. Would a saddle valve in the line be useful? If so, sshould it be installed at the highest or lowest point in the supply or return line?

      riw408@aolmcom

    • #289279

      Never use a saddle valve as when the piercing part gets blocked up it is USELESS

      Best way replace the 90 degree fitting on the end to a “Baseboard TEE then install a proper manual bleeder