water pressure

Home Forums Public Forums General Plumbing water pressure

Viewing 2 reply threads
  • Author
    Posts
    • #274155
      Avatar photoMasterPlumbers
      Keymaster

        Your assumption about above ground city water tanks etc. are correct.
        Should I replace my relief valve with one rated higher, or may this cause other problems. Suggestions?
        Thanks

      • #289265
        Avatar photoHarold Kestenholz
        Participant

          If your relief valve is rated around 70 psig, then IMO I would keep it at that. If a manufacturer supplied the water heater that way then it is best to follow the manufacturer’s design. The relief valve may not have a temperature sensor on it so there is no security about a runaway overheat condition. If there is no temperature probe on the existing relief valve, you could add a long T&P valve into the tank opening with a 3/4-inch street tee and then add the old 70 psig pressure relief in the branch.

          You can add a domestic water diaphragm expansion tank to the water heater to insure that there will be air in the bladder to take up the expansion. The expansion tank for domestic water has an inner coating to prevent oxygen from rusting a hole inside the tank within a year. In this manner, the tank expansion remains independent of the air quantity in the water.

        • #289266
          Avatar photoSylvanLMP
          Participant

            If there is no temperature probe on the existing relief valve, you could add a long T&P valve into the tank opening with a 3/4-inch street tee and then add the old 70 psig pressure relief in the branch. Harold this is true BUT dont you think you should have added that the T&P valve Probe SHALL BE located in the uppermost 6″ of the tanks hottest water AND the Probe should be EXTRA long to make sure it is immersed inside this hot water to make sure it does sense the hottest water?

            Even a few inches in a closed tank can make a big difference in actual temperature.

            The problem with MOST cold water “relief” valves is there is no means to test them.

            Have a FANTASTIC week end Harold