        Hello I have 3-zones for the house, I think I have air in the line for the kitchen. when the room calls for heat the zone pump runs, and you hear the water running, but now heat from the base board heater. How do I get the air out of the lines?? (Bleed the line) how????

      • #289161
        Avatar photoHarold Kestenholz
        Participant

          By closing the other zones and opening the kitchen zone only, water can be forced through the air-filled zone tubing to force the air bubbles out. Then the system can be closed off to continue running with less air.

        • #289162
          Avatar photorburman
          Participant

            Thank you: each zone has it’s own pump and thermostat, each time the pump runs and I open the air bleeder nothing comes out, but when the pump is not running, water comes out of the bleeder when opend

            quote:


            Originally posted by Harold Kestenholz:
            By closing the other zones and opening the kitchen zone only, water can be forced through the air-filled zone tubing to force the air bubbles out. Then the system can be closed off to continue running with less air.


          • #289163
            Avatar photoHarold Kestenholz
            Participant

              Look at the piping layout at http://www.aresinc.com/Hydronic/multcirc/multcirc.htm
              to see the difference in the arrangement of the pupms and expansion tank. When the pumps pump toward the expansion tank, you get the symptoms that you describe. There a more expansive explanation at http://www.aresinc.com/Hydronic/Des/start.htm#Positive