Hot water heater

Home Forums Archives Old Bulletin Board Archives Hot water heater

Viewing 2 reply threads
  • Author
    Posts
    • #280942

      Occasional venting from relief valve. Have 15-yr-old State, model Courier electric. Anyone have idea: thermostat, element, relief valve?

    • #304168

      Depending on the amount of venting, it could be a failing relief valve, excessive house pressure, thermal pressure buildup due to a PRV or check valve in the supply line, over heating due to bad thermostat or element. So you can see that you have a shopping bag of possible options, but replacing the relief valve would be the first one since they should be replaced every three or four years anyway.: Occasional venting from relief valve. : Have 15-yr-old State, model Courier electric. : Anyone have idea: thermostat, element, relief valve?

    • #308651

      I am trying to locate a state, model courier gas hot water heater. Must have the following measurements….height


      36 diameter —- 20 to 22 capacity —- 30 to 40 gallon Need the short size for installing in addick…Anyone know any dealers having this model?

Viewing 2 reply threads
  • The forum ‘Old Bulletin Board Archives’ is closed to new topics and replies.

Pin It on Pinterest

Share This