    • #280942
      Avatar photofred

        Occasional venting from relief valve. Have 15-yr-old State, model Courier electric. Anyone have idea: thermostat, element, relief valve?

      • #304168
        Avatar photoJohn Sadler
        Participant

          Depending on the amount of venting, it could be a failing relief valve, excessive house pressure, thermal pressure buildup due to a PRV or check valve in the supply line, over heating due to bad thermostat or element. So you can see that you have a shopping bag of possible options, but replacing the relief valve would be the first one since they should be replaced every three or four years anyway.: Occasional venting from relief valve. : Have 15-yr-old State, model Courier electric. : Anyone have idea: thermostat, element, relief valve?

        • #308651
          Avatar photoJohn Sadler
          Participant

            I am trying to locate a state, model courier gas hot water heater. Must have the following measurements….height


            36 diameter —- 20 to 22 capacity —- 30 to 40 gallon Need the short size for installing in addick…Anyone know any dealers having this model?