      What is the drop for the drain line from the house to the septic tank.Thanks

    • #303520
      Avatar photoMack
      Participant

      : What is the drop for the drain line from the house to the septic tank.: Thanks

    • #303521
      Avatar photoMack
      Participant

      : What is the drop for the drain line from the house to the septic tank.: Thanks First I would check local codes. AS a thumb rule 1/4 inch per foot for 3-inch diameter and less,and not less than 1/8 inch per foot for diameters of 4 inches or more.