Water Heater tripping fuse.

Home Forums Public Forums General Plumbing Water Heater tripping fuse.

Viewing 3 reply threads
  • Author
    Posts
    • #273339
      MasterPlumbers
      Keymaster

      I have erf90-52/fre90-52 water heater
      which trips frequently the circuit breaker of 30 Amps. It is advisable to
      raise the circuit breaker to 40 Amps?

      On the heater, I don’t see any specs
      for circuit breaker.

    • #287398

      The water heater are 4500W, so you would draw about 20 Amps. Breakers are usually sized at 1 and 1/2 times the rated amps. Doubling the overload will remove some of the safety feature and may violate code. There might be a problem element or a decaying breaker; it is better to replace the bad part than to defeat your safety feature.

    • #287399

      Dont increase your amp setting, the idea is that the fuse blows, if you raise the amp then the chance of heating up the cable to the unit increases, and may cause more problems, get a electrition to look at it

    • #287400
      hj

      None of the wiring in the water heater is designed for 40 amps. You have a defective element that needs replacement.