      Getting a discharge from the pressure releif valve

    • #302612

      : Getting a discharge from the pressure releif valveT&P s (Temp & Pressure) are set for 210 degrees, boiling, and 150 PSI. First thing I check is the water pressure. If pressure is more than 80 pounds, than a PRV should be installed. A system with a check valve on it will allow the hot water to expand and build pressure. If a check valve is causing excessive pressure buildup a expansion tank should be installed. If pressure is below 80 pounds, replace the T&P

    • #302615

      : Getting a discharge from the pressure releif valveFYI Replaced valve,problem continued , then found both heating elements bad… with top element shorting to ground,in effect keeping it heating when the thermostat turned it off

    • #305741

      : Getting a discharge from the pressure releif valve

    • #303206

      : : Getting a discharge from the pressure releif valve: FYI Replaced valve,problem continued , then found both heating elements bad… with top element shorting to ground,in effect keeping it heating when the thermostat turned it off