    tomckey wrote:
    …What diameter pipe should I use?

    4″ diameter soil pipe should be sufficient for your application.

    …How would I connect the ABS into a cast iron bell?

    I don’t know why your plumber recommended hub and spigot CI drain pipe…maybe that’s what he’s cutting into. Frankly, no-hub CI pipe would make more sense, and can be connected to other pipe with no-hub or Fernco type fittings. You could transition from the bell with a section of CI hubless pipe that’s either leaded into the bell or inserted with a neoprene compression fitting, and you can carry on from there with either no-hub or Fernco.

    What would be the best way of dealing with the existing toilets and sink drains. Meaning, do I replace all current pipe with plastic, or would I connect the current cast pipe to the ABS, and if so, what is the best way of doing so. Not just to be up to code but if there is a best way, I want to do it that way.

    There may be no “best way.” But try to make it easy on the next person who has to work on your system. Generally speaking, hub and spigot CI drains are not easy to work on, so go with hubless/Fernco fittings.

    Also, where are the appropriate places to put cleanouts? I would guess that I need one where the line is going to go through the foundation and another where each of the drain stacks meet the main line. Do I need additional cleanouts before or after the pipe turns for the corners or along the long (close to 50 foot) run? Thank you for any help.

    Cleanouts are specified by the plumbing codes (UPC, etc), based on cumulative bend angles and run lengths.

    Hope this helps.

    NtP