Pedestal Sink Drain

Home Forums Public Forums Drainage & Sewerage Pedestal Sink Drain

Viewing 3 reply threads
  • Author
    Posts
    • #279312
      Avatar photoMasterPlumbers
      Keymaster

        The pedestal is open from the sink to the floor. Can I run the drain pipe down through the floor and put the trap benwath the floor? I have access to the area below the floor

      • #300518
        Avatar photoRetired plbg1
        Participant

          No the trap has to be at the fixture, that kind of Plumbing went out with the Romans. Also has to be vented.



          Art retired plbg

        • #300519
          Avatar photonicktheplumber
          Participant

            It would be OK per the IRC if the vertical leg is less than 36″…for sink lavs this would allow a trap just under the floor (IRC 3105.3).

            NtP

          • #300520
            Avatar photonicktheplumber
            Participant

              After reviewing the codes, I’m now not sure if my previous post is correct. Both the IRC and UPC specify a 24″ maximum length for a fixture tailpiece into a trap. I believe that I was confusing an exemption in the codes for washing machine standpipes. Nonetheless, what’s good for the goose would seem to be good for the gander. Although the codes do seem to prhibit lav tailpieces > 24″, I’m not sure that llwngths up to 36″-42″ wouldn’t function properly, except of course they would be “against code.” I’d appreciate any comments from my plumbing brethren on this.

              NtP

          Viewing 3 reply threads