Rate of slope on stool line to septic tank

Home Forums Public Forums Drainage & Sewerage Rate of slope on stool line to septic tank

Viewing 1 reply thread
  • Author
    Posts
    • #278520
      Avatar photoMasterPlumbers
      Keymaster

        We are trying to install a new sewer line (approx. 18 ft.) from the stool to the septic tank…we have a 1.6 gal.stool and need to know the slope for the new line.

      • #298680
        Avatar photohj
        Participant

          If the pipe is 3″ then 1/4″ is the minimum. If 4″ then you can reduce it to 1/8″ per foot.

      Viewing 1 reply thread
      • You must be logged in to reply to this topic.

      Pin It on Pinterest

      Share This