Home › Forums › Public Forums › Gas & Gasfitting › GAS PIPE SIZE
- This topic has 5 replies, 4 voices, and was last updated 23 years, 11 months ago by fourth year.
-
AuthorPosts
-
-
29 Jan 2001 at 12:08 am #278133MasterPlumbersKeymaster
I have a building needing a gas line .I have a total of 360,ooo btu.The total length of the line is 65 feet.I figure the pipe size to be 1 1/2 inches.Is this correct? Thank You
-
29 Jan 2001 at 4:06 am #297786SylvanLMPParticipant
What gas pressure and what is the specific gravity of this gas, is this LPG or natural.
AND what is the heating value of the type of gas your using.
Some natural gases can be as low as 900 BTU per CU ft and some as heigh as 1,200
-
29 Jan 2001 at 4:20 am #297787SylvanLMPParticipant
quote:
Originally posted by [email protected]:
I have a building needing a gas line .I have a total of 360,ooo btu.The total length of the line is 65 feet.I figure the pipe size to be 1 1/2 inches.Is this correct? Thank You
Ok based on a pressure drop of 0.3 inch water column and 0.6 specific gravity of the gas and a deeveloped lenth of 65 ft you could use an 11/4 pipe so the 11/2 would be fine.
Check with your local gas supplier and building department to be sure.
You are better off slightly over sized in case you add any more appliances later. Good luck
-
29 Jan 2001 at 3:06 pm #297788Frank HiebertParticipant
I will give you two different scenario’s, both based on natural gas with a specific gravity of .6, but different pressure. I have used a developed length of 70′.
For gas pressure of 7″ to 14″ water column, based on a pressure drop of 1/2″ wc . Schedule 40 pipe, 1 1/4″ will allow you 440,000 btu’s, 1 1/2″ pipe will allow you 659,000 btu’s.
For gas pressures of 2psig, schedule 40 pipe based on a pressure drop of 1 psig. 1/2″ pipe will allow 503,000 btu’s for 70′.
These numbers are based on the Canadian gas code and are here only for an example to you. You should definitly have a lisenced gasfitter correctly size and install this for you, as there are many other variables that will come into play, and codes to follow for the proper installation and testing. Good luck
Frank Hiebert
3rd yr apprentice
Edmonton, Alberta -
30 Jan 2001 at 12:57 am #297789SylvanLMPParticipant
Hi Frank, FYI in NYC any gas pressure exceeding 1/2 PSI is considered High pressure.
-
30 Jan 2001 at 3:02 pm #297790fourth yearParticipant
In AZ, 3 to 5 pounds is medium pressure. Usually the only time the utility will supply medium pressure to a house is when corrugated stainless tubing is installed for the gs system. And then each appliance has to have a pounds to inches regulator installed.
-
-