        does anyone know the procedure for putting in a new pressure relief valve in a kenmore power miser 12, 50 gal. hot water tank?

      • #295639
        Avatar photoDUNBAR
        Participant

          Turn water off at cold inlet valve above the water heater.

          Shut electric off or turn gas valve to pilot.

          Open T&P where the spring clip holds open.

          Open boiler drain below at bottom of tank and drain about 10 gallons of water out of tank.

          Unscrew drain pipe attached to T&P.

          Use pipe wrench and turn valve counter clockwise to remove.

          When reinstalling relief valve, use teflon tape on the threads before installing new one.

          Follow the above instructions in opposite to get water heater back to functioning.

          Check your water pressure. It might be causing the leak.



          “Your best interest is secured by making the right decisions the first time.”

        • #295640
          Avatar photoSelgas
          Participant

            Dunbar

            Heck, even I can follow them there instructions – well done.



            Selgas Services Ltd
            Craftsman Gasfitters, Plumbers, Electrical Service Technicians

          • #295641
            Avatar photoPLUMBILL
            Participant

              If your t&p valve is leaking you might need a expansion tank.