Home › Forums › Public Forums › General Plumbing › exhaust gas venting
- This topic has 3 replies, 4 voices, and was last updated 23 years, 8 months ago by gaston.
-
AuthorPosts
-
-
16 May 2001 at 2:17 am #274954Jim Miller
I have a water heater that sits approx. 3 ft from an outside wall in my basement. The flue goes to the outside at a 45 degree angle and vents out the side of my house. When the wind is blowing at the front of the house I get significant backflow into the house. Many times the pilot light will extinguish. What can be done besides purchasing an new direct vent water heater to prevent this from happening. I am wondering if there are kits for converting my water heater to a direct vent, or if something else can be done. I was thinking of a heat sensor that turns on a blower? Any suggestions.
-
16 May 2001 at 3:28 am #290820
-
16 May 2001 at 1:31 pm #290821fourth yearParticipant
You do not have a problem when the burner is operating, so unless you also installed a damper in the flue, which would be illegal under a lot of codes, a blower would not help your problem. You have an illegal flue, since it is supposed to rise to a point above the roof line, but in any case not terminate through a side wall. Do you have a Belmont cap on the flue and a draft diverter on the water heater?
-
16 May 2001 at 5:01 pm #290822gastonParticipant
quote:
Originally posted by fourth year:
You do not have a problem when the burner is operating, so unless you also installed a damper in the flue, which would be illegal under a lot of codes, a blower would not help your problem. You have an illegal flue, since it is supposed to rise to a point above the roof line, but in any case not terminate through a side wall. Do you have a Belmont cap on the flue and a draft diverter on the water heater?
I don’t know what the Belmont cap or the draft diverter is? I have a standard cap on the outside wall that prevents rain from getting in the top. The top of the heater has a adapter that is wider than the ehaust ducting, I think this is standard. I had asked the inspector about exhausting on the side wall and they approved it. May be they did not know that this should not be done.
If the burner is operating and there is some back flow, I believe some of the exhast gases may be coming in the house until the flow reverses after about 5 minutes or less.
-
-
AuthorPosts