Reply To: Oil/forced air heating problem

Home Forums Public Forums General Plumbing Oil/forced air heating problem Reply To: Oil/forced air heating problem

#290453
Avatar photoGuest
Participant

    The relay is a band-aid fix. The chimney should be large enough to handle both appliances at the same time. It may be that the burner nozzle is too large, making the combined fires too much for the chimney. The relay would let the larger appliance fire and perhaps force the gases backwards into the water heater, making soot there.

    There are books on CD about oil service available at
    http://www.notaei.org or
    http://www.hydronic.net

    The National Fire Protection Association has books for chimney sizes according to the combined inputs of appliances, the chart may be in the instructions that came with the appliance. An experienced plumber can follow these directions. In any case, find an experienced burner technician to set up your fires safely.