Reply To: Pin hole leaks in copper

Home Forums Public Forums General Plumbing Pin hole leaks in copper Reply To: Pin hole leaks in copper

#287910
Avatar photoSylvanLMP
Participant

    1. Water at high velocity can cause this condition.

    High water velocity may be caused by an
    undersized piping system, causing erosion that can cause this to take place.

    The real solution is to lower the water velocity. Like a throttling valve (Globe pattern) by lowering the velocity of the water in the system you save undue wear on the internal tubing walls. You can also opt for a pressure reducing valve BUT they can be a real pain in the neck to service and globe valve keeps it simple to adjust.

    The relationship is as follows:

    Reduce pipe size, increase velocity; increase pipe size, reduce
    velocity. Recommended velocity for hot water in a copper tube system is 4 –
    5 feet per second (fps). If systems are designed to respect these velocities
    the piping will last a very long time trouble free. Cold water piping could be slightly higher 2. Numerous, abrupt changes in direction in the piping system. Where
    structural conditions cause numerous directional changes, long radius (1.5
    Diameter) fittings should be used to minimize the interruption of laminar
    flow.
    3. Lack of reaming the tube ends. Burrs left on the ID of the tube can
    cause interruption of laminar flow resulting in localized high water
    velocity and cavitation.

    4. Protrusions into the flow stream caused by excessive lumps of
    solder/brazing material, improperly fabricated tees (branch protruding into
    the run pipe), etc. These protrusions can also cause the
    interruption of laminar flow resulting in localized high water velocity and
    cavitation.

    5. Excessive water temperature. Heating water above 140 degrees Fahrenheit
    can accelerate the process of erosion/corrosion. As the temperature
    increases, the velocity should be lowered. At 180 degrees Fahrenheit, the
    velocity should be down around 2 – 3 feet per second (fps). ( 180 I use on commercial, industrial and institutional and heating jobs)

    Bear in mind that these conditions are not peculiar to copper tube, but can
    affect other materials as well. However, when erosion/corrosion does occur
    in copper tube it is readily identifiable by the horseshoe shaped pitting
    throughout the inside of the tubes. Identification OD these pits or grooved
    corrosion-product-free areas on the inside of the tube can help you
    determine that water velocity is too high and that the reduction of velocity
    can correct the condition.

    Sorry if I got carried away with too much technical jargon, but it is the only way to express the proper way to correct this problem and I think if you have a better picture of what’s going on it helps you with options.

    You could also consider having your water tested for the pH value as copper cannot take hard water or acidic and water treatment program may have to be set up.