      The construction on the house is build a 2 level/family Modular Home. We have hot water heating system and for each floor with 2 zoning for their boiler (in the basement). The 2nd floor appears to have serious banging noise on one of the baseboard in the bedroom and some banging in through out the house. The weird thing is it only bangs/hammering at night during certain time at night (11pm till early AM time). We kept the thematic at 73 and leave it untouched to see if the banging and hammering occurs at the same time every night, which confirmed to be yes. Our plumber came to bled the systems several time and still not helping at all.
      Please help me!!
      Thank you,

    • #297249
      Retired plbg1
      Participant

      Sounds like he did not get all the air out of the pipes.



      Art retired plbg

    • #297250
      Selgas
      Participant

      Sounds like air hammer to me meaning that the installer has not completely bleed all the air from the system and or one of the radiator valves has a washer jumping in it.