Explain the units thing?

Home Forums Public Forums General Plumbing Explain the units thing?

  • This topic has 2 replies, 3 voices, and was last updated 24 years ago by Avatar photoSylvanLMP.
Viewing 2 reply threads
  • Author
    Posts
    • #272787
      Avatar photoMasterPlumbers
      Keymaster

        Got this code check book, and every
        thing seems to be in units ie, 2″
        trap arm= 2 units and tubs= 2 units
        ect. when I look at the sizing drains and vents, a vert. 4″ =256
        drain units? I interpet this to
        mean that a 4″ vert. drain can have a max of 256 units. but that must mean that every foot of pipe is equal to so many units, and that fittings are so many units ect.
        can one of you point me in the right direction on this? Thanks Kevin

      • #286297
        Avatar photohj
        Participant

          Every plumbing fixture has an equivalent fixture unit rating, which is what you are looking at. Length of piping does not have a relationship to units except that the longer the pipe, the fewer units it can handle in some cases. Your code book will have a table which gives those fixture unit equivalents. A lavatory is the basic standard at one unit. Bathtubs will be 2 or 3 depending on where you are located. Toilets will be 6 units, etc..

        • #286298
          Avatar photoSylvanLMP
          Participant

            A FU ( fixture unit) is a measurement plumbers eng etc size waste and vent piping. A fixture unit is 1 cu ft of water (7.48 gallons) and this FU is timed going down a drain pipe. For
            example a basin is ONE FIXTURE UNIT as it contains a max of 7.48 gallons and it will empty ideally in one min. Then you have roof drainage Square feet which normally is 3 Sq Ft = 1 FU after the normal sizing table is used,
            AND the pitch of the roof which predicates the leader sizing, more pitch more FU’s

            Again depending on local codes and rain fall conditions based on a 10 year chart.

            The only time you have to concern yourself with FU in developed lenth is for vent piping, as for waste or soil lines you base the FU on the pitch of the pipe and diameter.

            The Vertical is based on the soil/waste stack FU chart NOTHING to do with developed lenth.

            If your sizing water lines then you must figure the total fixture demand and again as per local codes size your water lines accordingly. (cold water lines normally larger)

            Water lines are a little more complex as you have friction losses to calculate in finding the proper FU peak demand as well as hydrostatic losses (.434 height and to figure how high a certain pressure will elevate water you take 2.31 PSI will give you an approx height the water will go LESS FRICTION LOSSES for developed lenth of piping and fittings and valves

            When sizing a pump ( sump pump/ sewerage ejector) discharge a lot of codes calculate ONE GPM as 1 FU.

            The problem with over sizing the drainage/soil/ waste piping is erosion of the piping and not getting the proper scouring action needed to keep build up to a min.
            Too much velocity on the horziontal will cause excessive piping erosion on ferrious and non ferrious metal piping systems PLUS the noise factor (especially on garbage plastic systems)

            The vent piping can be oversized with no adversed condition.

            Remember one thing about “plumbing” the final responsibily is the licensed master plumber for the proper pipe sizing NOT the engineer or the
            architech. If the system is wrong then the plumber has to face full responsibility and rightfully so.

            This seperates the REAL PLUMBERS from the dabblers and bums out there. Have fun



            SylvanLMP

        Viewing 2 reply threads
        • You must be logged in to reply to this topic.

        Pin It on Pinterest

        Share This