Reply To: Pumping public water over hill

Home › Forums › Public Forums › General Plumbing › Pumping public water over hill › Reply To: Pumping public water over hill

#287591
Avatar photoSylvanLMP
Participant

OK lets try this. 40 PSI pressure would equal a height of 92.4 feet and even then the water if it made it that high would only trickle out at best.

So lets figure WHAT kind of use this water is going to serve pressure and volume wise?

Are you supplying just a faucet that requires 6 PSI to operate OR a flushometers that requires a minimum of 25 PSI or several fixtures or a sprinkler system?

So without knowing ANYTHING lets assume you need about 100 PSI at the final outlet.

150 FT converted to pounds pressure would be around 65 PSI. JUST to get to the top.

Then figure the head the pump has to over come (Height and weight of the water) and your Demand in GPM.

OK lets go with an 11/4″ pipe and a TDH of 200′ to over come friction losses and flow rate of 40 GPM. I would go with a 3450 RPM Bronze body or stainless steel close coupled pump compatible to a Federal pump 1 CG 5 horse power.

If I had more information to work with I could be more exact.

At any rate I wouldn’t even consider a 1750 RPM pump for this kind of height.

If indeed your TDH is around 180 feet your GPM flow would increase
to 50 GPM with approximately 100 PSI USING 11/4″ piping.

Not knowing your piping materials such as plastic or copper or steel I can only over size this pump as each material has a different flow characteristics as far as friction is concerned.

And you though plumbing was just changing a washer HUH?