Normally you when Install a new automatic feeder, they are factory set at 12-15 PSI
outlet pressure.

OK here is where it gets tricky. If you take the pressure times 2.31 it will tell you how high this will elevate the water.

Also on systems where your not sure how much pressure you actually need, try to do the following.

Measure from the boiler to the top of my highest radiator and take this number and times it by . 434 (no flow conditions) BUT also add another 10 ft of static head so you know you have a positive pressure in this system (keeps air out)

Example 50 ft static head . 434 = 21.7 PSI

To prove take 2.31 times the pressure 22 PSI would equal 50. Ft approx.

Add the fudge factor and then size your expansion tank accordingly as when this water is heated it will expand.

To find the total gallons required to fill this system, All you do is drain it filll it up through a water meter and it will give you the measurement in cubic feet (7.48 gallons) this would you help you in sizing the actual volume your dealing with.

Personally I love open tank systems as you know you have a constant head pressure. Air in the system will find its way to this open tank and NOTHING mechanical to fail. Of couse it this tank does leak flood city LOL ( hey you cant have everything)