Home › Forums › Public Forums › General Plumbing › Ejector pump installation › Reply To: Ejector pump installation
18 Feb 2000 at 5:33 am
#285824
Participant
The shut off valve, whether gate or ball, is normally only needed in a two pump situation where you will want to isolate a pump whicl it is being serviced. In a single pump situation, it is of value only when you need to take the check valve out and do not want to drain the water from the riser pipe onto the floor.