Reply To: corrosion of copper pipes

Home › Forums › Public Forums › General Plumbing › corrosion of copper pipes › Reply To: corrosion of copper pipes

#287292
Avatar photoGuest
Participant

quote:


Originally posted by GaryPurolite: You have stated the case quite well. Pin hole leaks and high metallic content in the water are the result of an internal corrosion process most commonly called Electrolysis.
This post has drawn much interest, and is a subject dear to my heart. I have been a Plumbing Contractor for 51 years, and have spent a great deal of time tilting at the pin hole Windmill.
I first became interested in the pin hole problem in the 60’s. It is hard to maintain credibility with your customers if you repair a
pin hole leak under a slab or in a wall only to return in 6 wks. or 6 months to repair another 6″ or so from the earlier repair site.
By degree is in Bus.Adm. and did
not help at all in the search for answers for this growing plague of pin hole leaks.
I was very fortunate to have had
the talents of really smart cookies in Metallurgy and Electro-Chemistry at my doorstep. During the 60’s my section of Florida was awash with highly skilled people who had been working in the space
program contractors. As things started to wind down in that area, there was an abundence of skilled
people in need of employment. I hired a man who wrote technical
manuals for the astranauts working
at a Super Market rounding up shopping carts.
I had as a kid worked for Consolidated Edison in metro NYC. My job there was to install Zinc anodes to protect the gas distribution lines from attack from corrosion. And learned the basics of cathodic protection by means of the sacrificial anode principle that had been around a hundred years or so.
During the Korean War I served with the 127th Airborne Engineers, and fell into the job of protecting
Missle Silos from corrosion.
In 1953 I moved to Florida and have been a Plumbing..Gas..Utility
Contractor since.
I became aware early on that most pin hole leaks occur in the cold water piping ( unless it is hot water recirculation line with high velocity water whizzing through it 24 hrs. a day).I guessed
this might be due to the presence of the Aluminum or Magnesium anode that is to be found in virtually all water heater.
I enrolled in night classes in
Chemistry and Physics, so I could get a better handle on the interaction of pH values and ambient DC current on the inside of a closed plumbing system.
I thoroughly digested the electroplating analogy and electro desolution scales. There was an still is a myth that if you have a perfect 7 on the ever popular pH scale, you and your copper pipes will have a long and happy life.
In the desert South West people
drink Alkali water with a pH of 9+.

If the water in your very own piping system has the ability to conduct an electrical charge(and it does), it is an electrolyte no
matter the pH.

If your very own piping system has any DC voltage present, (and it does) You have all that is needed to get into the pin hole biz. The DC voltage is really tiny
and is measured in Milivolts. A Milivolt is 1/1000th of a volt.
There is a great deal of disagreement as to where this mystery voltage comes from, and depends in large part on who you ask. I have an opinion from whence it comes, and will be happy to share that with you after class.

Here in essence is what happens inside the piping system…….

For simplicity sake imagine your entire piping system as one contiuous 3/4″ type “L” copper tube
500 feet long. The water enters at “A” and travels through and discharges at “Z” by way of a #74 boiler drain into a covered container.

Turn the water on so that there is a flow of 1 gallon per minut(approx). coming out of the boiler drain.

Take an 8’copper clad ground rod an
drive it all the way into the ground at the mid point of your 500 foot water line, but don’t connect it to the water line. Now
connect the black lead of your new
digital volt/ohm meter to that ground rod. The black lead is 250
long so that you will be able to walk back and forth over the entire length of your water pipe.

Set the digital Volt/Ohm meter to the 20 milivolt function. Now stroll up toward the “A” end of the pipe, every few paces take the red lead and touch it to the copper water line. Take those little adhesive tags I gave you and
write the milivoltage value on it and stick it on the pipe. You have 50 tags to use 25 on either side of that mid point will give the best overall information..if the
milivolt reading goes off scale, turn the function knob to a higher
setting and continue sticking dem tags.

You will notice a great disparity
in voltage readings as you wander up and down the pipe. I have found
readings as high as 2000 milivolts
(2000 milivolts is 2 Volts)

If you remember your high school chem. 101, you will recall that
electrical charges are analogous to Mother Natures dislike of vacuums. An area of higer electrical potential will travel by any means available to a lesser
charged area. The means of travel in our scenario is by way of our electrolyte (water) that is flowing
through the pipe.

Ions are positively charged particles that would like to establish an electrical balance in side the pipe. As these Copper ions are detatched from the wall of the copper pipe, the copper leaches into the water. If there is chlorine in the water, you will be getting some green stains in the covered container eventually.
If there is any sulfur in the water blue stains from copper sulfate can be expected.

The DC electricity is the force that drives this corrosion process, the water aids and abets in this by transporting the copper scrap. This process is 24 hrs. a day for years or decades but eventually a hole will be munched through the wall of the pipe and a pin hole leak will be born.

The more voltage difference within
a given piping system and or the more efficient the electrolyte, the more copper you will be drinking and the more pin hole parties you will be invited to.

This is not a perfect world we cannot always control the quality of the water that is delivered to us. And there is not a whole lot that can be done about the unwanted electrical energy that finds it way to our piping system and induces the copper to leave home.

We can take the cowardly approach of tossing the baby to the wolves.
The Sacrificial anode concept is just exactly that ie it allows the Magnesium anode to be consumed by the vicious copper eating wolves.
As long as ther is an available meal for the critters, they will spare the copper..kinda like plate glass insurance.

The hardest part of the development of the Copper Knight was the never ending difficulties of getting a NSF certification.
Bud Hardman
Suncoast Plumbing Inc.
Sunny Florida
State Certificate
CFC037167

Holy smokes people. There are lots of causers of pin hole leaks in copper pipe. Low pH of 6.2 is just one. This person could have in addition to that any number of other causer’s. If Bud has a device that can resolve all of them in one felled swoop, God Bless Him. He should be a very wealthy man very soon.

Some causes:
Low pH – Less than 7

Electrolysis – caused by dissimilar metals, stray electrical currents or grounding of electrical wiring to the pipe. These are aggrevated by high Total Dissolved Solids (TDS) in the water.

High Chlorides in the water – Over 25 ppm.

High Oxygen content.

Extreme water flow velocity.

Low pH is the easiest to treat by installing a Calcite Neutralizing Filter. This will neutralize that pH to somewhere slightly above 7.

The other causer’s need to be confirmed by water analysis and by plumbing inspection. Contact a local Masterplumber and a local Water Treatment Specialist and hopefully they will work together to resolve your problem. Whatever it is.