The radiator valves on a hot water system (Hydronics) DO NOT shut off the water to the radiator as these valves have a hole drilled in the cylinder OR gate. The reason the hole is there is to prevent FREEZE UPS.THEY are meant to CIRCULATE water constantly!!!

The proper way to drain this type of system is to shut the boiler switch FIRST.

2nd SHUT off the water supply leading to the boilers automatic feeder (PRV) then drain the boiler including the expansion tank.

As the system drains your going to have to open a bleeder valve on and upper floor to break the vacuum

AFTER the water stops flowing you still will have some pretty dirty water still in the radiators that will not drain completely in most cases. By watching your altitude gauge you can tell when the system is down.

When refilling use the automatic feeder and LET the water get to room temperature before switching the boiler back on so as not to cause thermo stress. Watch yuor gauge and bleed each radiator BEFORE letting the circulator work. Have fun