Home › Forums › Public Forums › General Plumbing › Double lav drain › Reply To: Double lav drain
4 Jul 2000 at 3:00 am
#286996
Participant
Each Lav must have its own trap and each trap must be with in 2 ft of a vented line.BUT the fixture can be as far as 2 FT from the trap so in reality you have 4 feet to play with.
Vertically you can drop no more than 48″ CHECK local codes to be sure. I never use “wet vent” garbage. Individual venting is the way to be a professional
