M sorry Gerry I am so used to hearing from brain dead folks like “Jack” and his home center mentality that I did over react.
Ok when you told your LMP your going to install a fire place did you give him/her any idea of the BTU input rating?
Another thing is HJ is 1 million percent correct with the use of flexible piping as opposed to the black steel going through a floor
About the manufacturers reccommendations read the fine print where it sayslocal codes will prevail.
Now as for your 25 years in the construction trades Fantastic as I was a roofer/plumber/welder/shipfitter/stationary engineer/ general contractor and IM STILL learning everyday.
For your peace of mind in the future you should have a local plumbing code book so you know if the installing plumber is following the LOCAL code in the area.
I feel HJ is also correct with the location of shut off valve (approved ball type gas valves are GREAT)
OK Gerry now REMEMBER local codes prevail ok? I am NOT second guessing your LMP or YOUR mechanical abilities
. “My question was can I hook directly into the hard pipe at floor level or do I need to go vertically and then horizontally [with a drip leg] and then back down to the hard piping that runs into the appliance”
If your coming up through the floor YOU can place the drip leg ( IF REQUIRED) below the floor in the basement. Picture a “T” the drip leg would be on the “run” of the tee the straight through part not the middle (bull) connection so your drip leg would be normaly the vertical part with a cap on it from the bottom of the run ??? I hope you got what I said
The purpose of the drip was intended to catch moisture in natural gas as manufactured gas is drier. This drip leg was placed on piping either going vertical OR suppose you had gas lines in the ceiling and you supplying gas to a hot water heater in the basement? The piping drop would require a drip leg as condensation could be supplied to the heater and thus extinguishing the flame and the drip leg would catch this before it could cause problems.
My original post had to deal with a little bit on knowledge as these “Jack” leg mentalities had installed DRIP LEGS outside of a commercial building not realizing IF there was moisture in the winter these lines could freeze RUPTURE and allow the gas to be brought back into the building via the heating/AC system.
I personally try to use black steel schedule on all my gas piping and use a left and right nipple and coupling in lieu of a union as JACK (legs) will try to play with them causing a leak.
After the piping is installed PRIOR to final hook up I strongly suggest you pressure test all piping with “AIR.” Gerry if you have any questions please feel free to send me an E mail and your more then welcome to join my plumbers discussion group.
We not only have a full fledged chemist on the list (he owns a drain cleaning company) we have engineers and manufacturers.
Your more then welcome to post Questions and answeres and become an active member. Have a great one
US GC’s have to stick together LOL