Reply To: Flue Size Follow-Up

Home › Forums › Public Forums › Gas & Gasfitting › Flue Size Follow-Up › Reply To: Flue Size Follow-Up

#297598
Avatar photoSylvanLMP
Participant

Lou, a lot of codes will allow you to use the existing chimeny under certain conditions.

One of the main conditions is getting a A licensed Chimney sweep to clean out the old soot from the chimney/ flue as oil burning equipment Oil heat is a wet heat fuel as compared to the drier Natural gas heat

The problem is the soot build up could cause a flue fire or sulfuric acid to become a problem..
Now FYI a lot of the commerical and big building boilers I installed are duel fuel nat. Gas/ # 2 oil so they do use a common chimney.

They key again is to find out if local codes will allow the licensed chimney sweep to give you a letter saying the existing chimney has been properly inspected and cleaned. Good luck