Reply To: Direct Vent Water Heaters

Home › Forums › Public Forums › Gas & Gasfitting › Direct Vent Water Heaters › Reply To: Direct Vent Water Heaters

#297562
Avatar photoBrandon Seward
Participant

An A.O. SMith Power vented heater with 3-90 degree fittings can run out to 40ft in developed lengh! Must use long turn 90 degree
fittings or 45’s. 4ft from any fresh air inlet/window. Look into vent location before purchasing!! FInd out where a good location is!