Given the information you have now advised I am almost certain that your problem with the Infinity is due in the main to a lack of gas supply pressure or volume. Contact your gas supplier and have them check out the outlet supply pressure from your gas meter set and when they are undertaking that test turn on the hot tap on full and let them check the pressure drop. My logic behind this consideration is simply that you have suffered a similar problem allbeit not so often with your central heating unit which would be caused by the same problem – this problem usually only shows itself when the weather is really cold and the meter regulator does not react to the demand request fast enough. A similar problem can be the result of undersized gas piping but if this were the case then problem would be there everytime you tried to start both the water heater and the central heating unit at the same time. I really suspect the meter set is your fault – particulary we are now into the winter cooler months where meter diaphrams often fail due to the outside air temps.
Have the check done and let me know the outcome please.