You might be surprised at “residential” pressure readings. There is a neighborhood here in Cincinnati in which the pressure can climb as high as 200psi during the night (Dunbar knows where I’m talking about….right around Spring Grove and Winton Rds).
First check the static pressure. You should be getting a reading of less than 80psi (I have my own house set at 65psi). If it is more than this then check the pressure reducing valve…if there is one at all. These can and do go bad over time and can be readily replaced. If your friend doesnt have a pressure reducing valve and the pressure reading is more than 80psi then get one installed.
In addition, with a PRV you’ll also need an expansion tank. Water expands as it is heated and in a closed system it has no place to expand to thus creating excess pressure on the system causing the T&P valve to release.
Finally, the T&P valve itself may or may not be at fault itself. These too go bad, are inexpensive and very easy to replace. Anytime I get a call for a T&P leaking I like to go ahead and replace them even if they arent the source of the problem. Often, once a T&P releases it wont seat properly anymore. Much easier to replace it with an expansion tank and/or PRV than to get a call a couple of days later saying I didnt “fix” the problem.
Good luck