Reply To: Vent offset from fixture branch

Home › Forums › Public Forums › General Plumbing › Vent offset from fixture branch › Reply To: Vent offset from fixture branch

#296926
Avatar photoCincinnatiPlumbing
Participant

The vent is to rise vertically to a point at least 6″ above the flood level rim of the highest fixture served before making any horizontal offset. After this point it can be directed to the local vent stack using 22-1/2s, 45s, 60s, 90s or any combination thereof.

» This message has been edited by CincinnatiPlumbing on 13 October 2005