I note you say you do not have an expansion tank fitted – that being the case the water contained within the gas cylinder is heated by the burner and expands, in doing so the pressure and temperature relief valve operates to protect the entire system. Once it opens it discharges hot water to waste. Over time these valves become less acurate and begin to fail – down here we recommend that the TPR valves be replaced at intervals not less than 4 years for this very reason. Sounds to me like a simple replacement valve will put things back to where you were originally. If your Plumbing code allows the non use of an expansion tank you could fit a cold water relief valve to the inlet cold water pipe just before the cylinder which should be set at 70% of the ppressure the hot water valve is set for. This will make the expansion take place on the cold water inlet line and push mainly cooler water to waste thus saving you costs in wasted energy.
Selgas Services Ltd
Craftsman Gasfitters, Plumbers, Electrical Service Technicians