This condition happens a lot where the installing plumber doesn’t not allow for the proper sizing of the flushometer piping and also fails to use a dedicated line just for these flushometers

You can try to run a separate line (dedicated) strictly for flushometers as flushometers require around 25 PSI min and a flow rate of around 25 GPM

Picture a garden hose going full blast. Now picture this same hose with a double connection see the drop in pressure and also the volume as you splitting this in half.

A flushometer is a great device BUT unfortunately a lot of contractors try to cut corners with under sizing the supply lines to this fixture. Another problem associated with flushometers using an undersized line is the flow rate Velocity in FPS which, on copper tubing can cause erosion if left unchecked ( no more than 8 FPS is recommended)