For those of you who are interested in this topic, I will provide the NEC citation: you will find it at 250-104a,b. This basically requires ground bonding jumpers between all hot,cold, and gas piping so that if any of these becomes accidentally energized dangerous currents will be diverted to ground. This is the rationale behind ground bonding jumpers across water meters, water heaters, and other things that may electrically isolate sections of the metallic plumbing system.
This really is an important safety issue, and I’m surprised by the number of times I’ve come across (mostly older, but not always) installations where this had been overlooked. It’s always easy to fix with a couple of pipe-groind clamps and a bit of 6-8 guage solid copper ground wire.
NtP